281 Results
A
  • RANK

    PMC Rank N Alarm

  • RANK Description

    This is an alarm generated by the NC control device.

  • Cause

    All alarms from NC.

  • Solution

    Action according to the alarm number displayed on the display device.

A
  • RANK

    PMC Rank N Alarm

  • RANK Description

    This is an alarm generated by the NC control device.

  • Cause

    NC battery voltage drop.

  • Solution

    Battery replacement with NC power on.

A
  • Cause

    M, S, T, B functions are locked

  • Solution

    Set D10.0 at ‘0’.

A
  • Cause

    Oil is running out in Lub. Oil tank.

  • Solution

    Reset key after oiling

A
  • Cause

    Lubricant pump works but setting pressure is not achieved in the limit time

  • Solution

    Check for cause at unit and reset it.

A
  • Cause

    Chuck manual works during main spindle rotation or hold status or auto operation

  • Solution

    Operate chuck in spindle stop, manual mode (reset)

A
  • Cause

    Sensor does not detect chuck CLAMP, UNCLAMP for specific time at model with main spindle sensor

  • Solution

    Adjust sensor position and check for operating status of sensor

A
  • Cause

    Main spindle rotation command is given when MAIN CHUCK is not Clamped

  • Solution

    Give spindle rotation command after main chuck CLAMP .

A
  • Cause

    Set K0.7 at ‘1’ (slide way lubricant pump does not work.)

  • Solution

    Set K0.7 at 0.

A
  • Cause

    No manual zero return after releasing machine lock

  • Solution

    Use after manual zero return.

A
  • Cause

    Cycle starts during T/S QUILL inching or when it is not at FOR. REF. position

  • Solution

    If there is a QUILL sensor, check for sensor position or give command to move QUILL to correct position.

A
  • Cause

    Cycle start is performed in Unclamp status at Model with Manual T/S Base.

  • Solution

    Clamp T/S Base and then operate it.

A
  • Cause

    T ? CODE command is given that is not supposed to given.

  • Solution

    Check for THE NUMBER OF ANGLE OF TURRET. Check for commanded T-CODE (In case of K2.0 = 0, EX2113 alarm occurs when T0 command is given.)

A
  • Cause

    HYD' TURRET is UNCLAMPED and failed to CLAMP in 5 seconds.

  • Solution

    1. Check if TURRET is at CLAMP position. 2. reset and manually move it and then check for the correct position. 3. In case it is not at clamp position by manual move, position adjustment of A phase B phase Z phase sensor is required. 4. If TURRET is in

A
  • Cause

    Z phase is not On when Turret gets at position of tool #1.

  • Solution

    Check for operating status of Z phase SENSOR of TURRET. If SENSOR works normally, move TURRET be each angle in manual mode to set point at which Z phase SENSOR is detected as tool no 1.