281 Results
A
  • RANK

    PMC Rank I Alarm

  • RANK Description

    Only the device is limited in motion and there is no obstacle to axis traversing.

  • Cause

    Run maintenance mode for ATC arm and ATC Magazine together.

  • Solution

    When the maintenance mode is released, it is automatically released. ATC Magazine is useful when using Servo.

A
  • RANK

    PMC Rank I Alarm

  • RANK Description

    Only the device is limited in motion and there is no obstacle to axis traversing.

  • Cause

    Voltage drop in the battery inside the work probe.

  • Solution

    Internal battery exchange. When the voltage is normal, the alarm is automatically released.

A
  • RANK

    PMC Rank I Alarm

  • RANK Description

    Only the device is limited in motion and there is no obstacle to axis traversing.

  • Cause

    After selecting the work probe, the ready state signal is not input within 1 second.

  • Solution

    Check work probe wiring and settings.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    When the slide Lub pump is operating, the internal breaker is blocked due to overload.

  • Solution

    After removing the cause of the error of the breaker (QM46) setting value or more overcurrent, check the operation status.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    Coolant cooling unit alarm.

  • Solution

    Check the unit's instruction manual or maintenance manual.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    External cooling unit alarm.

  • Solution

    Check the unit's instruction manual or maintenance manual.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    External work counter completion alarm.

  • Solution

    After resetting the counter direction of the external work counter, it is restarted.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    Cycle start is executed while the feed override switch is set to more than 100%.

  • Solution

    Switch set to 100% or less. When the switch exceeds 100%, cycle start is possible. K value change.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    Automatic operation is executed when all axes have not established the origin.

  • Solution

    Establish the origin of all axes.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    Automatic operation is executed when the ATC Arm is not in the correct position.

  • Solution

    After positioning the ATC Arm correctly, execute.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    Automatic operation is executed when the spindle is not clamped.

  • Solution

    After clamping the spindle, run.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    Automatic operation is executed when ATC Magazine is not in the correct position.

  • Solution

    After checking the location of ATC Magazine, run.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    Automatic operation is executed when the magazine port is not in the correct position.

  • Solution

    Check if the port position is on the spindle side or the magazine side, then run.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    When operating the slide Lub pump, the pressure does not reach the set value within 20 seconds.

  • Solution

    Check for pipe damage and air in the pipe. Check the pressure signal.

A
  • RANK

    PMC Rank S Alarm

  • RANK Description

    Limits on cycle start.

  • Cause

    The oil level inside the slide Lub pump remains low for more than 2 seconds.

  • Solution

    Filling the tank with oil. Check the operation of the water level sensor inside the tank.